Water leaking from Condesate exhaust pipe outside of furnace??

Started by wantboost, December 02, 2020, 03:16:17 PM

Previous topic - Next topic

wantboost

What section of code is this?
A or b tag ?
No CO leaking into room
G2

Admin

I could understand if someone issued an A tag but personally I would issue a B tag.  Maybe reduce the days to 15, on the B tag, to be certain it's fixed before it became an immediate hazard.

I believe you have done your diligence and proved it's not an immediate hazard.

wantboost

G2

Admin

For a B tag use,

QuoteClause 4.1.3 - An appliance, accessory, component, equipment, or any other item shall be installed in accordance with the manufacturer's certified instructions and this Code.

The venting installation manual would require that the joint be properly glued.

For an A tag use,

QuoteClause 4.5.2 - The use of an appliance, accessory, component, equipment, or material shall be prohibited where a hazard is created.

wantboost

Up to tech to decide how many days ??
Also whats o.reg # ?
G2


wantboost

The tag that ubpisted in that link doesn't even ask for a o.reg # ? Maybe mine are old....


Quote from: Admin on December 07, 2020, 12:10:02 PM
You decide how long for a B Tag.  Enbridge allows up to 42 days.

https://hvactechgroup.com/article.php/20150501132753661

Ontario Regulation 212/01 and 215/01 are 2 regulations you should read.

https://www.hvactechgroup.com/hvacforum/index.php?topic=325.0

https://www.hvactechgroup.com/hvacforum/index.php?topic=1212.0
G2

Admin

Did you read O.Reg 212/01?  No where does it say the warning tag must specify O.Reg 212/01.

The rules for issuing a warning tag are very clear.  Just read that regulation.

wantboost

I ll post a pic of the tags i have later . Thx

Quote from: Admin on December 10, 2020, 04:04:39 PM
Did you read O.Reg 212/01?  No where does it say the warning tag must specify O.Reg 212/01.

The rules for issuing a warning tag are very clear.  Just read that regulation.
G2

Admin

That's probably a TSSA tag.  Both tags are fine to use.

All you have to do is what is listed in O.Reg 212/01 Section 13(3) and Section 14(3).

wantboost

Yup that is what I was trying to get an.  Hpw this one asks fornthrno reg #

Thx
G2