Clause 8.14.8(e)

Started by Hgye, July 11, 2018, 07:23:15 PM

Previous topic - Next topic

Hgye

Clause 8.14.8
A vent shall not terminate
(d) above a regulator within 3 ft (900 mm) horizontally of the vertical centreline of the regulator vent outlet to a maximum vertical distance of 15 ft (4.5 m);
(e) except as required by Clause 8.14.8(d), any distance less than that of any gas pressure regulator vent outlet as detailed in Table 5.2


Does this mean a furnace vent must be 10' away from a source of ignition?

NoDIY

10ft is for a mechanical air intake clearance from a regulator vent


Follow Table 5.2

Hgye

Table 5.2 says a propane regulator vent must be at least 10' away from a source of ignition.

8.14.8(e) says an appliance vent cannot be any closer than that of a regulator vent to anything in table 5.2

Doesn't this say that to follow 8.14.8(e), one must follow table 5.2 for a furnace vent?

NoDIY

 propane ok.. sorry i assumed NG

Table says 3ft for appliance vent outlet(exhaust) and 10ft for the furnace intake(appliance air intake)

Neither intake nor the exhaust are considered sources of ignition.


Hgye

Ok.  I get it now, thanks.  I was reading it that appliance vent has to have the same clearances as a reg.  The wording could be changed on it a bit to make it more clear.  Either that or I am getting a bit senile!