Secondary Heat exchanger test

Started by raptorman, September 22, 2009, 05:39:08 AM

Previous topic - Next topic

raptorman

I was in touch with carrier tech support regarding how to properly check the secondary heat exchanger.
I was told to do a flue gas test and if the c02 was over 8.5% for nat gas (10.5% lpg) the secondary was defective!

Has anyone else heard of this and does this apply to all secondary heat exchangers??

Thanks

Admin

Yeah I use those figures as well.  The best test is still a visual one, if you remove the blower you can use a mirror or scope to check the top side for cracks.  Usually you'll have pressure switch lockouts or flame roll out with a good crack.  ICP uses plastic headers that crack on the top side.

raptorman

I would like if people that read this give me feedback.
this could help us all.

acefurnacefixer

Its a hell of alot easier to just pull the blower and look at it, or if you have a see-snake u can look down through the high limit hole.........




I dont know about up in canaDA, but here in the states we are finding that about 99% of these units are failing.

Hgye


Admin

I posted a few stories regarding the Carrier heat exchanger problems in our General News section - Here

The lawyer who won the class action suit has some info posted - Here

Our province, Ontario, was also a part of the lawsuit, regarding Carrier secondary heat exchangers.

I also find alot of failure on the primary heat exchangers, on both mid and high efficiency models.  Just remove the primary limit and run your index finger over the golf ball sized indent.  Usually you will see or feel the crack.

Visit the Private Heat Exchanger for more examples.

acefurnacefixer


keeptheheatup

I came across the same problem a week ago . I did a flue analysis and had to pull the flue probe out because the co was to high. Upon further    inspection found the secondary to look just like  acefurnacefixer pic.

Admin

Download the Carrier Service Bulletin SMB 09-0022 - Here

612Rob

I've been told that there is a possibility you will not get an elevated CO reading on a cracked H/E but you will get the elevated CO2 readings.

Admin

It's true, but like I said in your other post, analyzing flue gas at the termination is useless.  It has to be done before the gasses enter the venting.

Only when a crack causes flame impingement or incomplete combustion will you get high CO readings.